Attended a 24ri a few days ago with just the blue light flashing - would not fire & was working up until yesterday.
Worcester fault sheet suggested:
Gas pressure
Co2 levels
Electrodes
Gas coils
Possibly pcb.
In other words could be anything.
I picked up a set of electrodes & a gasket.
On removal the rectification electrode was a bit short but the electrodes were sparking.
Removed the fan & found part of the rubber flap in the air-gas mixing chamber was missing. The other bit had passed through the fan & was sitting in the bottom of the burner.
Another merchant visit new flap installed & boiler rebuilt.
Still exactly the same fault.
Both coils tested & good resistance 35v being sent by board so all ok there. Gas pressure 23mb but noticeably no drop when the boiler was trying to fire. I would have expected a good 1 or 2 mb drop when trying to fire so deduced that the gas valve had also failed. Fortunately had a spare in the van which does several of the Worcester range.
Factory reset as a start point & apart from 440ppm it fired.
All adjusted to book Co2 settings.
In all about 5 hours including merchant visit.
So the fault sheet was more or less correct in that all those things were wrong with the exception of the pcb.
A bit unusual to get 3 parts fail at once, fortunately the customer was perched on my shoulder & could see each faulty part as they were uncovered.

Regards

Arthur

Love a good brain tease :D
 

Reply to Boiler Breakdown Sticky in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Had a call to a 82 Old man, he paid these £300 up front for a years cover, and I find out on arrival he's been waiting for 3 weeks, no heating or...
Replies
3
Views
606
J
On a breakdown which is stumping me. The boiler has no power to it even though everything else in the system is working as it should. The 3 way...
Replies
3
Views
617
Deleted member 120897
D
I have a clients oil Grant boiler I fitted last year. It is a Vortex pro 26-46 system. It is just a small system loop as it is a pool boiler...
Replies
10
Views
202
Hi do we need to do a gas rate or heat input when doing a boiler breakdown? Thanks
Replies
1
Views
893
G
Tiffel 20-50 boiler will not fire up. Screen shows ambient temp approx 20 degrees with a symbol of a flame. Got the settings just for hot water.
Replies
1
Views
74
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock