Hi
My oil boiler keeps locking out after running for 30/40 minutes! I then try to reset it but it won’t fire back up! I have to leave it for several hours before it will fire back up! Only to lock out again after 30/40 minutes!
The boiler has had a new nozzle, coil and pump in the last 2 weeks!

Any help or advice welcome
 
Temp and boiler lockout aren't linked.

You said that it would take hours to reset, what was it doing when you pushed the reset. What noises was it making?

Could be anything. But nothing a decent engineer can't sort.
 
Had someone back out and they changed the control box but didn’t work so put the old one back on! tighten up the terminals and it worked for 24hours now it’s gone back to locking out! Checked the terminals and there all tight!
 
Need to check if oil flow is good could be restricted so you get x amount of litres through then it runs out etc eg pipe kinked etc
 
Sounds like a mectron burner. You can hear it go through the ignition sequence and definitely no oil at point of ignition and locks out.
I'd first look at oil pressure whilst washing and also photo cell.
 