Sizing rads for ground source

Discuss Sizing rads for ground source in the Ground Sourced Heat Pumps Discussion Forum area at Plumbers Forums

Status
Not open for further replies.

TFGplumbing

Plumbers Arms member
Plumber
Gas Engineer
Messages
997
Hiya guys traditional heating systems work at ∆t50, so what do ground source heat pumps work at? ∆t25/∆t30; I need to size radiators for a customer with a heat pump as some of their existing ones are to small

Thanks
 
has the system been designed or is it a case of using the existing system and changing rads? if you have the heat loss calcs for each room then you shouldnt need to oversize the rads, just put in what is the required output for that room.
 
It depends what the design flow temperature is of the heat pump installation.

Also check flow rates are suitable as low flow could create poor performance.
 