Does anyone have experience of using a VR33 (for Heating OpenTherm control with Nest) and a VR66 for Hot Water Priority with Vaillant system boilers? I'm specifically using an EcoTec plus 624
I've got a system working with a Nest and VR66 to provide hot water priority and it works well with separate cylinder charge and heating flow temperatures. Currently this is all connected to the Nest using the switched CH and HW controls. I'd like to use the OpenTherm capability of the Nest for the heating but have questions about how the VR33 and VR66 coexist if they can at all. There is no timer or thermostat connected to the VR66. The only control input to the VR66 is the cylinder stat & nest HW switched line.
I'm hoping that the VR33 just behaves like an ebus thermostat and would work alongside the existing setup (with removing the switched CH controls on the boiler) but would love to know if anyone has experience of going into this level of detail.
 
Just doing this today. Just checking nothing connects the boiler to the vr66?

Are the nests connected to it?

I’m a bit confused by this too. Is the nest connected to the open term only and the vr66 still controls hw and heating under command from nest as putting in the vr33 changes ebus to opentherm? Why is the vr66 still required if nest can modulate over opentherm? Any help appreciated 👍🏻
 
Thank you for the info. I'll be in touch when I am ready to set it all up. I will be getting my old Potterton Supriema replaced with a Ecofit Pure 415 and my aim is to configure an identical setup like what you have managed to do with a VR10 NTC to keep the HW Cylinder topped up when the storage water temp drops below a set threshold. I have a single 3-port valve (s-plan) and just need to figure out which wires I need to connect to the VR66. If you have a pic as you know the saying goes. it will speak louder than words.
 
Has anybody managed to use the VR33 with Two zones i.e two Nests on OpenTherm ?

eg image below.
Nest 1 - Central Heading (CH) Ground Floor
Nest 2 - Central Heating (CH) Upper Floor AND Hot Water (HW)

If so, do you simply link the two Nests Opentherms (OT) together, like dives on a multiple master Bus ?
Certainly eBus connections can work like this, but I'm not sure about Nests and the VR33 Opentherm

Ideally, I would like to have
  • Nest 1 with a lower Target Temp (50) and Lower kWh, that better suits Underfloor Central Heating.
  • Nest 2 with a High Temp (75) for the HW Cylinder Charging and the Upper Floor Central Heating radiators.

If so, would you still need to use the Opentherm alongside the VR66/65 for Hot Water Priority ?

Screenshot 2023-04-20 at 09.16.45.jpg
 
Hi All, can anybody advise what is the correct set-up for SYSTEM Vaillant boilers?

Currently I have the boiler with a junction box for the valves and water cylinder and a classic room thermostat (Salus, On/Off type).

I have the vr33 module as well as a tado unit. Where do I go from there? Do I simply remove the old thermostat, plug the the vr33 on the PCB, and wire tado to the 2-pin connector of the vr33?

Or instead, does the vr33 need to be connected to the junction box somehow?

Thanks
 
Hi All, can anybody advise what is the correct set-up for SYSTEM Vaillant boilers?

Currently I have the boiler with a junction box for the valves and water cylinder and a classic room thermostat (Salus, On/Off type).

I have the vr33 module as well as a tado unit. Where do I go from there? Do I simply remove the old thermostat, plug the the vr33 on the PCB, and wire tado to the 2-pin connector of the vr33?

Or instead, does the vr33 need to be connected to the junction box somehow?

Thanks
I’ve just completed this install . Run a new 2 core cable from boiler to nest heatlink. Install vr33 believe it connects into x32 port . Connect the new wire to vr33 and nest heatlink, remove old thermostat. Setup nest as open therm
 
Hi All, can anybody advise what is the correct set-up for SYSTEM Vaillant boilers?

I’ve just completed this install . Run a new 2 core cable from boiler to nest heatlink. Install vr33 believe it connects into x32 port . Connect the new wire to vr33 and nest heatlink, remove old thermostat. Setup nest as open therm

This is an excellent question. How do you get Nest and VR33 to work together on a SYSTEM boiler, WITHOUT a VR65/VR66. Everyone else on this thread seems to describe how they use both VR33 and VR65 /VR66 Control Centre.

Here is my experience having done exactly as SamThor describes (and also bridged the RT24 and disconnected the RT240 live):

The CH is working with fine with modulation, but the boiler is not firing when there is DHW demand from the thermostat, neither is it applying the DHW temperature when both are running. My CW and DHW valves are still being controlled by the Nest thermostat and the DHW boost/charge signal is being sent via OpenTherm (D025 shows “Ext eBus signal: Cylinder charging: On” when there is hot water demand via Nest and off when there is no demand). However, the boiler refuses to fire up, presumably because it is not connected to VR65/VR66 to know the actual status of the valve/cylinder thermostat?

Has anyone managed to install VR33 and an Opentherm thermostat on a system boiler without a Vaillant Control Center? Thanks
 
This is an excellent question. How do you get Nest and VR33 to work together on a SYSTEM boiler, WITHOUT a VR65/VR66. Everyone else on this thread seems to describe how they use both VR33 and VR65 /VR66 Control Centre.

Here is my experience having done exactly as SamThor describes (and also bridged the RT24 and disconnected the RT240 live):

The CH is working with fine with modulation, but the boiler is not firing when there is DHW demand from the thermostat, neither is it applying the DHW temperature when both are running. My CW and DHW valves are still being controlled by the Nest thermostat and the DHW boost/charge signal is being sent via OpenTherm (D025 shows “Ext eBus signal: Cylinder charging: On” when there is hot water demand via Nest and off when there is no demand). However, the boiler refuses to fire up, presumably because it is not connected to VR65/VR66 to know the actual status of the valve/cylinder thermostat?

Has anyone managed to install VR33 and an Opentherm thermostat on a system boiler without a Vaillant Control Center? Thanks

I'd be happy to try things out Nick, I've ordered the module and a TADO smart thermostat. I also have a spare vr65, and currently wired via classic junction box.

The thing that puzzles me is how did the other guys manage to get it working even with the vr65.

From I understand what they did is:

1. Plug the vr33 on the PCB
2. run 2 core wire between their smart thermostat (Nest) and the vr33
3. run eBus between PCB and vr65
4. Connect the motorised valves to the vr65

If they manage to get control of DHW with this set-up, does it mean that when you select DHW with your phone, connect to the smart thermostat (Nest here), the smart thermostat will then communicate to the PCB via the vr33, which then sends a message through the PCB out to the eBus, which is then sent via eBus cable to the vr65, which will then tell the DHW valve to open and let hot water fill the tank?

That would also mean that the boiler now knows that DHW is ON and needs to stop modulating and heat more so the flow temp is above 60 degrees?
 
I was able to get the Opentherm, Nest and DHW priority to work once I also installed the VR66, which effectively eliminated the S plan system. The wiring in logic is exactly as you say above Plum47.
I have written about all the steps here in a clean thread (I can't link, you have to search for it)

Vaillant Ecotec system boiler with VR66 and Opentherm (Nest)​

 
I was able to get the Opentherm, Nest and DHW priority to work once I also installed the VR66, which effectively eliminated the S plan system. The wiring in logic is exactly as you say above Plum47.
I have written about all the steps here in a clean thread (I can't link, you have to search for it)

Vaillant Ecotec system boiler with VR66 and Opentherm (Nest)​

Hi, Do I need any of this if I am using Valliant ecotec pro combi boiler with VR33 OpenTherm and Nest ?
 
Hi, sorry to jump in. Do you mean the 24V RT connection bridge?
I am also thinking to connect Vr33 openTherm module to my Vailliant ecotec pro24 to work with Nest gen3.
Hi Daw

I think what @asoffe said is that if you remove the on/off type 230v control, and switch to a low voltage digital (eBus) connection, you should have a bridge on the "24v = RT" block on the PCB, which is a white block. Then you will connect your + and - on the eBus block if you want to use eBus, which is a orange / reddish block.

Hi, Do I need any of this if I am using Valliant ecotec pro combi boiler with VR33 OpenTherm and Nest ?

Tell us a bit more about what you currently have and what you are trying to do so we can try to help.
 
I'm setting up the VR66 and have installed the VR33.

Please can someone confirm how to wire 2 Nest stats for the 2 zone system I have. Do I put the VR33 OT wires to both NEST boxes?

Is two zone control possible with this setup. It's currently S plan with Unvented cylinder.

What version of VR66 did you use, there's VR66\2 which is most recent which they say has updated software.
 
I'm setting up the VR66 and have installed the VR33.

Please can someone confirm how to wire 2 Nest stats for the 2 zone system I have. Do I put the VR33 OT wires to both NEST boxes?

Is two zone control possible with this setup. It's currently S plan with Unvented cylinder.

What version of VR66 did you use, there's VR66\2 which is most recent which they say has updated software.

You can’t wire two nests in opentherm only one stat in the system
 
Really interesting thread - thanks for sharing experience/knowledge. My house was renovated ~10 years ago.
System comprises Vaillant 624 EcoPlus system boiler with 3 CH zones (rads up, rads down + UFH (HeatMiser UF3) ) plus HW in an unvented Main 210L tank); The UFH has 4 zones with 4 wall stats (as an aside, I think this is unnecessary now as the areas are mostly open plan so a single stat would suffice).
"Interestingly" the two rad zones share a common stat - I think this is fundamentally flawed but rather than fix it I'm looking to do a wholesale upgrade to get more efficient by using modulation + decent controls.

I've ordered a VR33 (FYI you need to create an account to get UK shipping - a guest can only do collect)
As per the excellent info, I was going to get the VR66* but am I right in thinking this will do HW plus one CH zone only?
If so the confusingly named VR61 seems to be twin CH zones + HW capable - could be used instead. is that correct? (I'll probably merge the rads up /down but TBD . I guess my final question is similar to James in that how would this (OT) work with two stats?

Thanks
 
You can’t wire two nests in opentherm only one stat in the system
Ah shucks. It means Ill have to do a standard S Plan, system boiler 2 Zone NEST setup.

So now I have a VR66, VR33 and VR10 NTC to off load as it’s no use to me.

Unless, does anyone know of any Opentherm programmer/thermostats that will deal the CH plus HW, and a 2nd upstairs CH zone?

Or equivalent Vaillant controls now that I have eBus routed to near the valves?
 
You could do weather comp and run the nests as stnd on off controls
 