I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump.

I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate) based on other parameters, my understanding is that auto balancing is only effective when their is constant flow.

Any help to demystify is appreciated
 
Except the pump menu has other settings then those two settings should mean what they say, if the pump has a 7M head at 100% then it will have a 7*(70/100)^2, 3.43M head at 70% speed but the flowrate through the system will be (70/100) or 70% of the 100% flowrate.
 

Reply to Auto balance trv and Ideal Vogue boiler in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

I currently have a 20 year old 24kW thermocompact system boiler which is costing a fortune to run. I have 13 radiators, hive TRVs and a total...
Replies
11
Views
1K
Hi all, I have an Ideal Logic max 35 and have just connected my Nest thermostat via opentherm. The boiler modulates the water temp fine but as the...
Replies
37
Views
5K
Hi everyone, I'm looking for some advice please. My system has 5 Drayton Wiser TRVs. There are 8 rads over 3 storeys and a 170l unvented...
Replies
10
Views
2K
I'll pop this into the general advice forum as it seems the most active, but mods - feel free to move if there's somewhere more appropriate. Thank...
Replies
18
Views
2K
J
  • Locked
Hi Everyone, I'm looking for a little advice so I can try and save a bit of money this winter (especially considering the new prices!) I have an...
Replies
5
Views
1K
Back
Top