Hi Guys

Just wanted to pick your brains on this one. (I'm g3)

Customer has a 250 litre un-vented cylinder in his loft. He called me to the blow off dripping outside.

The expansion vessel had failed and it was fitted at the bottom of the cylinder on the floor of the loft. The control valve was also ancient so I replaced the control valve and re-piped the inlet so the expansion vessel was above the cylinder.

3 months on and the blow off is dripping again. With a new control valve and expansion vessel.

The temperature and pressure relief valve appears sound. When I disconnected the new blow off on the control valve its definitely coming from there.

The un-vented cylinder is quite old. 15 years +

Would a split coil present like this? They have been losing pressure on the heating side.

This would be my first split coil on unvented, I've seen quite a few open vented but not on a sealed system.

Thanks
 
If you had a split coil on the unvented, your Heating would be increasing pressure not loosing. As the pressure of the cylinder is higher than the heating, so therefore would be introducing fresh water into the heating system. Unless of course your standing pressure is lower than 1.5bar.

Don't really see where the expansion vessel was fitted (Height wise) as long as it was fitted correctly.

What replacement control valve did you fit?

The other thing is, is the house piped on balanced cold? As otherwise a bar shower or something could be back feeding.
 
Problems causing PRV to discharge:
.Incoming pressure too high, ie, pressure reducing valve failed, or not one installed.
.Expansion vessel too small, lost some or all charge or too much charge.
.Defective PRV or bit of crap stopping from sealing properly.
.Unbalanced cold supply with mixer tap etc causing back pressure.

A split coil will just fill heating system due to the large pressure differential, unless of course as mentioned above cylinder static pressure is below heating system pressure but this wont happen.
 
Thanks I’ll look into back pressure. It’s looking like a tap or shower may have failed.

The control valve and expansion vessel were replaced like for like recently. I’m sure both are correct


One of my pet hates of unvented is expansion vessel at bottom of the cylinder as that means you have to drain the whole cylinder to repair or replace it.
 
Thanks I’ll look into back pressure. It’s looking like a tap or shower may have failed.

The control valve and expansion vessel were replaced like for like recently. I’m sure both are correct



One of my pet hates of unvented is expansion vessel at bottom of the cylinder as that means you have to drain the whole cylinder to repair or replace it.

Fit a valve and DC so you can work on it easily next time
 
Just popped in on the way home and the balanced cold of the control has been capped. So the back pressure theory is looking likely.

I just had a thought, could I just fit a 22mm double check valve on the dhw draw off?

Im also thinking of fitting a prv after the mains stopcock as it’s easily accessible in the garage.
 
Just popped in on the way home and the balanced cold of the control has been capped. So the back pressure theory is looking likely.

I just had a thought, could I just fit a 22mm double check valve on the dhw draw off?

Im also thinking of fitting a prv after the mains stopcock as it’s easily accessible in the garage.

Yes a DCV on HW outlet will stop any back feeding, if it doesn't solve the problem you know it lies elsewhere. Install a PRV on incoming mains will at least balance the supplies.
 
Just popped in on the way home and the balanced cold of the control has been capped. So the back pressure theory is looking likely.

I just had a thought, could I just fit a 22mm double check valve on the dhw draw off?

Im also thinking of fitting a prv after the mains stopcock as it’s easily accessible in the garage.
I'd fit PRV on Mains first and see if it cures it (Set at same a cylinder PRV), as in theory pressures will be balanced then theres little chance of back feeding. Which cylinder is it?

I've had the same before and done what you suggest with PRV on mains and it solved my issue.

Double Check valve on Hot Outlet would be last resort for me.
 
I fitted a 15mm prv on the incoming mains today. The mains runs about 1m in 15mm before teeing off and rising in 22mm. Not sure if I mentioned that the unvented cylinder is in the loft.

Well the cold supply is 22mm to the loft however the rest of the house is fed from the same supply as the unvented. Now the customer is complaining of pressure / flow loss on the cold taps, outside tap and the hot flow is significantly reduced when the downstairs taps are running.

I've tried to explain that this is a design flaw of the original system but they are adamant that fitting a 22mm prv instead of 15mm will improve things.... Thoughts?

I'm thinking 22mm dcv on the hot outlet from the cylinder and remove the prv. I've also mentioned installing a new dedicated 22mm main to the loft then connecting the balanced cold up there to the cold circuit.... this may also cause issues.

The standing pressure on the prv is only 2.8bar but we think the mains creeps up over 3bar during the night which would result in different pressures on the hot and cold
 
I fitted a 15mm prv on the incoming mains today. The mains runs about 1m in 15mm before teeing off and rising in 22mm. Not sure if I mentioned that the unvented cylinder is in the loft.

Well the cold supply is 22mm to the loft however the rest of the house is fed from the same supply as the unvented. Now the customer is complaining of pressure / flow loss on the cold taps, outside tap and the hot flow is significantly reduced when the downstairs taps are running.

I've tried to explain that this is a design flaw of the original system but they are adamant that fitting a 22mm prv instead of 15mm will improve things.. Thoughts?

I'm thinking 22mm dcv on the hot outlet from the cylinder and remove the prv. I've also mentioned installing a new dedicated 22mm main to the loft then connecting the balanced cold up there to the cold circuit.. this may also cause issues.

The standing pressure on the prv is only 2.8bar but we think the mains creeps up over 3bar during the night which would result in different pressures on the hot and cold
Main question is firstly, has it stopped your pressure relief from discharging?
 
So you have found the problem.
its getting a back feed from somewhere. I would be looking at shower mixers.
fitting a prv, is just sorting the symptoms. Not the cure.
Whilst you aren't incorrect I don't completely agree here, all supplies really should be balanced to showers/baths, and IMO most taps on a unvented system. So finding the back feeding culprit isn't really solving the issue completely as the pressures would still be unbalanced.

I know when retro fitting cylinders to existing houses you can't always do the balanced cold easily but then really a PRV should be fitted to the incoming main as the OP has done.

OP - The pressure decrease the customer is noticing - could any dirt have got in the PRV filter when you've fitted it or joint compound? 22mm might help with flow but then you really need to be making it a 22mm main too.

Really the main wants upgrading to 22mm to the unvented and then the balanced cold from the combination valve connecting into the rest of the cold supply. Know this probably isn't the easiest option.
 
As Chop says unvented cylinders require good incoming flow and pressure from supply outside of dwelling, quite often an unvented cylinder is installed, albeit by a G3 certified person but not always do they fully understand the requirements that need to be met in order to achieve the outcome that is expected. All outlets should be balanced, so the installation of a PRV as you did is not necessarily wrong, especially when 3 bar pressure is more than enough for most situations. I suspect the reduction in flow is down to inadequately sized supply piping, you may have good pressure but flow rates is largely down to size of pipes.
 