Good morning all, Did a CP12 yesterday and got 26 mbar Standing & 21 mbar working pressures at the meter so all good, but then found 22 mbar on the cooker burner and also 22 mbar at the inlet of the boiler??? Never come across a higher pressure at the appliance than at the meter before, Checked it three times to make sure with my U gauge and my FGA. Anyone else come across this before? Thought it was a bit strange.
 
How can you have more pressure working at the appliance when you only have 21 at the meter ?

External gas run ?
 
Hi Shaun, yes HOW I don't know. But you may have just answered my query. The meter was in a brick compartment accessed from a small wooden door on the outside of the building under the concrete stairs and it was a cold shaded little compartment. Whereas the pipework ran in 22mm for 4m external along the wall with the sun shining on it.
 
There you go heat will rise it 3-4 mbar

Bet your working was around 20 mbar
 
Thanks Shaun, 35yrs in the game and still learning. It is the first time I have ever come across this before. Wonder how many other GSR folk have come across it?

A few and I bet they phoned transportation up saying help :D
 