E
ed209
After advise regarding overheating and cutting out, I have removed both the F&R pipes in the boiler and flushed out, no blockage, blown through heat Ex with short length of hose seems clear, checked and cleaned by pass valve, there should be a filler but does not appear to be in there so either it has been removed in the past or broken up in to the system,
These boiler has a modulating pump and that has on occasion stopped and have had overheat but other times its carried on running I would say fast and strong enough to pump but still cut out
Apparently it was getting fault codes but not while I have been present just overheats, cools cycling
Cust cant remember what the codes were
Haven't tested for pump voltage yet going back tomorrow as I concentrated on initially the rubber pipe being blocked on the flow pipe as this was diagnosed as the problem by another engineer
No evidence of magnite being present
I keep thing it must be the pump or PCB not modulating
but would appreciate any advise
Thanks Paul
These boiler has a modulating pump and that has on occasion stopped and have had overheat but other times its carried on running I would say fast and strong enough to pump but still cut out
Apparently it was getting fault codes but not while I have been present just overheats, cools cycling
Cust cant remember what the codes were
Haven't tested for pump voltage yet going back tomorrow as I concentrated on initially the rubber pipe being blocked on the flow pipe as this was diagnosed as the problem by another engineer
No evidence of magnite being present
I keep thing it must be the pump or PCB not modulating
but would appreciate any advise
Thanks Paul