Can anyone confirm my thoughts on a solution to this boiler fault? Went to the above boiler yesterday and the hot water works perfectly until there's a demand for CH. The hot water keeps going cold when there's a demand for heating. The hall sensor was lighting on HW demand. I took off the motor head and the pin was moving but it was buzzing. Faulty intermittent motor or cartridge passing? The PCB has been replaced by a previous engineer who walked off the job.
 
So when the hot waters running when you create a central heating demand, the hot water fails?
 
So when the hot waters running when you create a central heating demand, the hot water fails?

Yep. That's correct. And when the CH is running if you turn a HW tap on, the HW water runs cold.
 
To my mind the diverter should prioritise the hot water. So the actuator shouldn't move. My first thoughts would be pcb, but that's been done.
The only other thing it can be is a small amount of voltage passing, and the actuater being weak.
I'd ring the tech help line up.
 
I did notice the Div motor buzzing (humming) so I removed it and noticed the spindle wasn't moving when switching, even when I tried to press the pin with a screwdriver, but after I pressed the pin a few times it moved. I re fitted the motor and all appeared to be working as it should,,,,,,,, but I got the dreaded call the next day to say it was exactly the same again. I've ordered a motor and a cartridge kit and I'm going to fit in that order and see what happens. It's jobs like these where you lose money and it's in our blummin nature not to give up. Thanks for reply Leo
 
Status
Not open for further replies.

Reply to Main combi 30 Eco DHW gets hot until... the CH is calling in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi Folks, I have a challenge with a Main Eco Elite 30 Combi which is short cycling on the CH. Water works fine. As soon as you have call for...
Replies
6
Views
442
M
Hi, Hopefully someone can throw some light on if this is a real issue or not. I have had this boiler for about 10 years, I noticed just recently...
Replies
1
Views
426
Hello, Looking for someone who can please help solve this problem and fix our boiler. Staffs area. CH seems fine. Boiler can be coaxed into full...
Replies
2
Views
738
Can anyone help me with an ongoing issue I've had since I had an annual service on my combi boiler, which is a Potterton Performa 24. Literally...
Replies
3
Views
381
Hi, My combi-boiler has just given up heating the house and basically only delivers hot water. While in central heating mode it heats up and stops...
Replies
2
Views
1K
Back
Top